General Category => TED Pro Support => Topic started by: klimber on September 27, 2015, 11:28:50 PM

Title: Maximum Spyders for TED Pro
Post by: klimber on September 27, 2015, 11:28:50 PM
Can I put 4 spyders on the pro?  I don't see a place to configure more than two spyders?  it seems like in some places documentation says that 4 will be supported in a future release?
Title: Re: Maximum Spyders for TED Pro
Post by: kherr on September 27, 2015, 11:37:15 PM
2 Spyders per MTU. 4 max per ECC
Title: Re: Maximum Spyders for TED Pro
Post by: klimber on September 28, 2015, 03:04:10 AM
thanks, so if I want to monitor 32 circuits what configuration would I setup?
Title: Re: Maximum Spyders for TED Pro
Post by: klimber on September 28, 2015, 03:07:39 AM
looks like I get a second MTU and put two new CTs on the power source like the existing ones?
Title: Re: Maximum Spyders for TED Pro
Post by: kherr on September 28, 2015, 03:14:05 AM
I would think you would just omit the second set or it would read double. Maybe wait and see if someone else chimes in on that one. Hope you have a lot of room.
Title: Re: Maximum Spyders for TED Pro
Post by: klimber on September 28, 2015, 03:20:25 AM
ok.

yeah, there is room but it will definitely get busy in the panel.
Title: Re: Maximum Spyders for TED Pro
Post by: klimber on September 29, 2015, 04:40:33 AM
Called them today and they confirmed what you said.

Buy an MTU and don't use the CTs.

I should have two more spyders and an MTU soon.

hopefully I can make the panel look organized with all the extra wires.  :-)
Title: Re: Maximum Spyders for TED Pro
Post by: kherr on September 29, 2015, 08:03:14 PM
Take your time and be sure to document as you go. You'll have a rat's nest after words ....